Q. 1
Electrical Engineering
Difficulty: Easy
(1 Mark)
An ideal transformer does not change:
💡
Step-by-Step Explanation & Concept Rationale
A transformer is a static electromagnetic device that transfers electrical energy from one circuit to another without changing the frequency (f1 = f2) and with 100% efficiency in an ideal case (P_in = P_out, V1*I1 = V2*I2).
Q. 2
Electrical Engineering
Difficulty: Easy
(1 Mark)
The EMF per turn in the primary winding of a transformer compared to the EMF per turn in its secondary winding is:
💡
Step-by-Step Explanation & Concept Rationale
From Faraday's law, induced EMF per turn is E1/N1 = E2/N2 = 4.44 * f * phi_m. Since the same mutual magnetic flux links both windings, the induced EMF per turn is identical in both primary and secondary windings.
Q. 3
Electrical Engineering
Difficulty: Easy
(1 Mark)
The open-circuit (OC) test on a transformer is performed to determine:
💡
Step-by-Step Explanation & Concept Rationale
The open-circuit test is conducted at rated voltage and frequency, typically on the Low Voltage (LV) side with the HV side open. Because no-load current is tiny (2-5% of rated), series copper loss is negligible, and the wattmeter reading directly measures the core (hysteresis + eddy current) loss.
Q. 4
Electrical Engineering
Difficulty: Easy
(1 Mark)
The short-circuit (SC) test on a transformer is conducted to measure:
💡
Step-by-Step Explanation & Concept Rationale
The SC test is performed at reduced voltage (typically 5-10% of rated) on the High Voltage (HV) side with the LV side shorted, circulating full-load rated current. Because the applied voltage and core flux are very low, iron losses are negligible, and the input power represents the full-load copper loss (I^2 * Req).
Q. 5
Electrical Engineering
Difficulty: Medium
(1 Mark)
A 100 kVA transformer has a maximum efficiency of 98% at 80% of full load. What is the ratio of full-load copper loss (P_cu_fl) to iron loss (P_i)?
💡
Step-by-Step Explanation & Concept Rationale
Maximum efficiency occurs when variable copper loss equals constant iron loss: x^2 * P_cu_fl = P_i. At x = 0.8: 0.8^2 * P_cu_fl = P_i -> 0.64 * P_cu_fl = P_i -> P_cu_fl / P_i = 1 / 0.64 = 1.5625.
Q. 6
Electrical Engineering
Difficulty: Medium
(1 Mark)
The condition for zero voltage regulation in a practical power transformer occurs at:
💡
Step-by-Step Explanation & Concept Rationale
Voltage regulation is approximate to (I2 * Req * cos(phi) +- I2 * Xeq * sin(phi)) / V2. For zero regulation, Req * cos(phi) - Xeq * sin(phi) = 0 (which requires a leading PF), yielding tan(phi) = Req / Xeq (leading).
Q. 7
Electrical Engineering
Difficulty: Medium
(1 Mark)
The maximum voltage regulation in a transformer occurs at a:
💡
Step-by-Step Explanation & Concept Rationale
Differentiating the regulation expression with respect to phi and setting to zero yields the maximum regulation condition: tan(phi) = Xeq / Req at a lagging power factor, meaning cos(phi) = Req / Zeq (lagging).
Q. 8
Electrical Engineering
Difficulty: Easy
(1 Mark)
Why are distribution transformers designed to achieve maximum efficiency at 50% to 70% of full load rather than at 100% full load?
💡
Step-by-Step Explanation & Concept Rationale
Distribution transformers are energized continuously (24 hours/day) with fluctuating consumer loads, averaging 50-70% capacity. Designing core loss to be very low and setting maximum efficiency around average load optimizes all-day energy efficiency.
Q. 9
Electrical Engineering
Difficulty: Easy
(1 Mark)
All-day efficiency of a transformer is defined as the ratio of:
💡
Step-by-Step Explanation & Concept Rationale
All-day efficiency (or commercial energy efficiency) is calculated on an energy basis: eta_allday = (Energy Output in kWh over 24 hours) / (Energy Input in kWh over 24 hours). It is vital for distribution transformers.
Q. 10
Electrical Engineering
Difficulty: Medium
(1 Mark)
In an autotransformer with transformation ratio k = V2 / V1 (where k < 1), the fraction of power transferred inductively through magnetic coupling is:
💡
Step-by-Step Explanation & Concept Rationale
In an autotransformer, total power is transferred via two mechanisms: conductive power = k * P_total, and inductive power = (1 - k) * P_total. The copper saving is k * (copper of 2-winding transformer).
Q. 11
Electrical Engineering
Difficulty: Medium
(1 Mark)
What is the primary operational hazard of leaving the secondary winding of an energized Current Transformer (CT) open-circuited?
💡
Step-by-Step Explanation & Concept Rationale
In a CT, secondary ampere-turns oppose primary ampere-turns (N2*I2 opposes N1*I1). If the secondary is opened, secondary MMF becomes zero, and the entire large line current acts as magnetizing current. This drives the core deep into saturation, inducing lethal peak voltages (thousands of volts) across the secondary terminals.
Q. 12
Electrical Engineering
Difficulty: Easy
(1 Mark)
The Buchholz relay is a protective device used in oil-immersed transformers to detect:
💡
Step-by-Step Explanation & Concept Rationale
A Buchholz relay is installed in the pipe connecting the main transformer tank to the conservator tank. Gas bubbles produced by slow internal arcing or overheating rise and trigger an alarm. Severe faults produce a violent oil surge that trips the circuit breaker.
Q. 13
Electrical Engineering
Difficulty: Easy
(1 Mark)
The silica gel breather attached to a transformer conservator tank serves to:
💡
Step-by-Step Explanation & Concept Rationale
As transformer temperature rises and falls, oil expands and contracts, causing air to breathe in and out. The silica gel crystals absorb moisture from incoming air to maintain the high dielectric breakdown strength of the insulating oil.
Q. 14
Electrical Engineering
Difficulty: Easy
(1 Mark)
Fresh, dry silica gel in a transformer breather has which color, and what color does it turn when saturated with moisture?
💡
Step-by-Step Explanation & Concept Rationale
Dry cobalt chloride-impregnated silica gel is deep blue. When it absorbs moisture, it chemically transitions to hydrated cobalt chloride, turning light pink, indicating it needs reactivation by heating.
Q. 15
Electrical Engineering
Difficulty: Medium
(1 Mark)
Which three-phase transformer connection is capable of converting a 3-phase supply into a balanced 2-phase supply for electric arc furnaces?
💡
Step-by-Step Explanation & Concept Rationale
The Scott connection utilizes two single-phase transformers: a main transformer with center-tapped primary (50% tap) and a teaser transformer tapped at 86.6% (sqrt(3)/2) of primary turns, effectively converting 3-phase to balanced 2-phase or vice versa.
Q. 16
Electrical Engineering
Difficulty: Medium
(1 Mark)
In an Open-Delta (V-V) transformer bank where one transformer of a 3-transformer Delta-Delta bank is removed, the remaining two transformers can deliver what percentage of the original bank's rated kVA capacity?
💡
Step-by-Step Explanation & Concept Rationale
The V-V bank capacity is sqrt(3) * V * I = sqrt(3) * S_single. Since the original 3-transformer delta bank capacity was 3 * S_single, the ratio is (sqrt(3) * S_single) / (3 * S_single) = 1 / sqrt(3) ≈ 57.7% (operating at 86.6% of the two remaining transformers' combined rating).
Q. 17
Electrical Engineering
Difficulty: Hard
(1 Mark)
The tertiary winding in a large Star-Star (Y-Y) power transformer is connected in Delta primarily to:
💡
Step-by-Step Explanation & Concept Rationale
In ungrounded Y-Y transformers, 3rd harmonic currents cannot flow, causing severe distortion in phase voltages and neutral oscillation. A closed Delta tertiary winding provides a circulating path for 3rd harmonic magnetizing currents, eliminating distortion.
Q. 18
Electrical Engineering
Difficulty: Medium
(1 Mark)
For two 3-phase transformers to operate successfully in parallel, which condition is ABSOLUTELY ESSENTIAL and non-negotiable?
💡
Step-by-Step Explanation & Concept Rationale
If phase sequence is incorrect or vector groups have phase displacement (e.g., Yd1 vs Yd11), a massive phase difference occurs across the secondary terminals, creating dead short-circuit circulating currents that will immediately destroy the transformers.
Q. 19
Electrical Engineering
Difficulty: Medium
(1 Mark)
When two transformers of different kVA ratings but equal per-unit leakage impedances operate in parallel, how do they share a common load?
💡
Step-by-Step Explanation & Concept Rationale
When per-unit impedances based on their own ratings are equal (Z_pu1 = Z_pu2), the ohmic impedances are inversely proportional to their kVA ratings. Consequently, load current divides such that each transformer carries load strictly proportional to its kVA capacity without overloading.
Q. 20
Electrical Engineering
Difficulty: Hard
(1 Mark)
Transformer magnetizing inrush current occurs upon energizing because:
💡
Step-by-Step Explanation & Concept Rationale
Since flux is the integral of voltage, switching on at a voltage zero-crossing requires flux to rise from 0 to 2*phi_m (flux doubling). In saturation, core permeability drops to near air permeability, resulting in inrush currents up to 6-10 times rated full-load current (predominantly 2nd harmonic).
Q. 21
Electrical Engineering
Difficulty: Medium
(1 Mark)
Harmonic analysis shows that transformer magnetizing inrush current is predominantly rich in which harmonic?
💡
Step-by-Step Explanation & Concept Rationale
Transformer inrush current has a strong unidirectional DC offset and asymmetric wave shape rich in the 2nd harmonic. Modern differential protective relays use 2nd Harmonic Restraint to distinguish inrush from internal short-circuit faults.
Q. 22
Electrical Engineering
Difficulty: Easy
(1 Mark)
In a core-type transformer, the low-voltage (LV) winding is placed closest to the iron core, with the high-voltage (HV) winding on the outside. Why?
💡
Step-by-Step Explanation & Concept Rationale
Insulating the winding against the grounded core requires dielectric insulation proportional to operating voltage. Placing the LV winding closest to the core minimizes insulation thickness and clearance distance, substantially lowering material costs and physical size.
Q. 23
Electrical Engineering
Difficulty: Medium
(1 Mark)
What is the standard test method used to determine the dielectric breakdown strength of transformer insulating oil?
💡
Step-by-Step Explanation & Concept Rationale
Under IEC 60156 standards, insulating oil BDV is tested across a calibrated 2.5 mm electrode gap. Good transformer oil must withstand at least 30 kV (and above 50 kV for high-voltage power transformers) without dielectric flashover.
Q. 24
Electrical Engineering
Difficulty: Hard
(1 Mark)
Sumpner's Test (Back-to-Back Test) on two identical transformers is conducted to determine:
💡
Step-by-Step Explanation & Concept Rationale
Sumpner's test connects two identical transformers with primaries in parallel and secondaries in series opposition. It allows operating both at rated flux and rated full-load current simultaneously, consuming only the internal losses (core + copper), enabling precise heat run testing.
Q. 25
Electrical Engineering
Difficulty: Hard
(1 Mark)
A 50 Hz transformer is operated on a 60 Hz supply of the same rated voltage. What will be the effect on its core losses?
💡
Step-by-Step Explanation & Concept Rationale
With constant voltage V, Bm is proportional to V/f = 1/f. Hysteresis loss P_h ∝ f * Bm^1.6 ∝ f * (1/f)^1.6 = f^-0.6 (decreases). Eddy current loss P_e ∝ f^2 * Bm^2 ∝ f^2 * (1/f)^2 = constant. Thus, total core loss decreases.
Study Stream Progress:
Showing 25 of 35 Questions (71%)
Jump to:
Ready to Test Your Retention & Speed?
Now that you have reviewed the study questions and rationales, test yourself in our interactive 1-by-1 practice engine or take the full official timed mock exam.